5.1.5 Fire Fighting equipment
Fire hose and nozzle.
Fire fighting hose shall be 2½” lay-flat type. Hydrant hose connections shall be female
2½” round threaded fittings to suit the hydrant outlet. Fire hoses shall be supplied in 30m
lengths of 3 per hydrant. Hoses shall be constructed in high tenacity polyester yarn with
a high grade steam vulcanised synthetic rubber lining, fabricated to DIN 14811 & prEN
1924-1.
The hose nozzle shall incorporate a jet control/shut-off valve. Nozzles shall be 2½” inlet
and manufactured from Aluminium alloy with the tip in a polymide material.
Fire hose couplings and lay-flat hose shall be in accordance with BS 336 and BS EN
671-2, as supplied by:
Angus Fire Ltd.
Thame Park Road
Thame
Oxfordshire
OX9 3RT
United Kingdom
http://www.angusfire.co.uk
Email: general.enquiries@kiddeuk.co.uk
Tel: +44 (0)1844214545
Fax: +44 (0)1844213511/2
Or approved equivalent.
Fire Equipment Cabinets
Fire fighting equipment shall be stored / located within designated permanent fire
fighting equipment cabinets unless otherwise directed. The requirements for the fire
fighting equipment cabinets are set as following;
The Contractor shall supply and install permanent cabinets for storage of all fire fighting
equipment (hose reels, nozzles, valves keys, hose wrenches and the like). An
equipment cabinet complete with the above fittings shall be installed adjacent to every
above ground hydrant. The equipment cabinets shall be sized 750 x 750 x 300mm and
constructed from 1.5mm hot dip mild steel galvanised sheet; red powder coated. A
break glass shall be provided to enable entry to the cabinet in addition to a key locked
entry facility. The cabinet shall include a central window (sized 260 x 260mm) to view
the contents, internal hose reel support pin, stand and base fabrications.
Each cabinet shall contain
• 3 hose lengths
• Hose wrench
• Valve wrench
• 3 hose nozzles
• 1 foam free extinguisher (as outlined in clause 5.4)
• 1 dry power fire extinguisher (as outlined in clause 5.4)
• 1 CO2 fire extinguisher (as outlined in clause 5.4) 展开
Fire hose and nozzle.
Fire fighting hose shall be 2½” lay-flat type. Hydrant hose connections shall be female
2½” round threaded fittings to suit the hydrant outlet. Fire hoses shall be supplied in 30m
lengths of 3 per hydrant. Hoses shall be constructed in high tenacity polyester yarn with
a high grade steam vulcanised synthetic rubber lining, fabricated to DIN 14811 & prEN
1924-1.
The hose nozzle shall incorporate a jet control/shut-off valve. Nozzles shall be 2½” inlet
and manufactured from Aluminium alloy with the tip in a polymide material.
Fire hose couplings and lay-flat hose shall be in accordance with BS 336 and BS EN
671-2, as supplied by:
Angus Fire Ltd.
Thame Park Road
Thame
Oxfordshire
OX9 3RT
United Kingdom
http://www.angusfire.co.uk
Email: general.enquiries@kiddeuk.co.uk
Tel: +44 (0)1844214545
Fax: +44 (0)1844213511/2
Or approved equivalent.
Fire Equipment Cabinets
Fire fighting equipment shall be stored / located within designated permanent fire
fighting equipment cabinets unless otherwise directed. The requirements for the fire
fighting equipment cabinets are set as following;
The Contractor shall supply and install permanent cabinets for storage of all fire fighting
equipment (hose reels, nozzles, valves keys, hose wrenches and the like). An
equipment cabinet complete with the above fittings shall be installed adjacent to every
above ground hydrant. The equipment cabinets shall be sized 750 x 750 x 300mm and
constructed from 1.5mm hot dip mild steel galvanised sheet; red powder coated. A
break glass shall be provided to enable entry to the cabinet in addition to a key locked
entry facility. The cabinet shall include a central window (sized 260 x 260mm) to view
the contents, internal hose reel support pin, stand and base fabrications.
Each cabinet shall contain
• 3 hose lengths
• Hose wrench
• Valve wrench
• 3 hose nozzles
• 1 foam free extinguisher (as outlined in clause 5.4)
• 1 dry power fire extinguisher (as outlined in clause 5.4)
• 1 CO2 fire extinguisher (as outlined in clause 5.4) 展开
展开全部
5.1.5灭火设备
消防喉及喷嘴。
消防软管应2 ½ “停工的单位类型。消防栓软管连接应女性
2 ½ “轮螺纹接头,以适应消防栓出水口。消防喉,应提供在三十米
长度为3 %的消防栓。软管应兴建中的高韧性聚酯纱
一高品位蒸汽vulcanised合成橡胶衬里,编造符合DIN 14811 & pren
1924-1 。
软管喷嘴应纳入喷射控制/切断阀。喷嘴应2 ½ “进
和制造由铝合金与提示,在聚酰胺材料。
消防喉联轴器及裁员单位的软管,应按照符合BS 336和BS恩
671-2 ,提供的:
安格斯消防有限公司
thame园道
thame
牛津郡
ox9 3rt
联合王国
http://www.angusfire.co.uk
电子邮件: general.enquiries @ kiddeuk.co.uk
电话: +44 ( 0 ) 1844214545
传真: +44 ( 0 ) 1844213511 / 2
或经核准的同等学历。
消防设备机柜
灭火设备应储存/位于指定的永久性防火
战斗设备机柜,除非另有指示。要求消防
战斗设备机柜设定为以下;
承包者应提供并安装永久柜储存的所有救火
设备(消防喉辘,喷嘴,阀门钥匙,胶管扳手等) 。 1
设备内阁完成与上述设备应安装毗邻每
地上消防栓。该设备机柜应大小750 x 750 x 300毫米和
兴建从1.5毫米热浸镀锌碳钢板;红色喷粉。字母a
打破玻璃应提供给使进入内阁中,除了一个关键锁定
进入设施。内阁应包括一个中央窗口(大小260 x二百六毫米) ,以查看
的内容,内部消防喉辘的支持PIN ,立场和相应的捏造。
每个内阁应包含
• 3软管长度
•胶管扳手
•阀门扳手
• 3软管喷嘴
• 1泡沫免费灭火器(概述在第5.4 )
• 1干的权力灭火器(概述在第5.4 )
• 1二氧化碳灭火器(概述在第5.4 )
消防喉及喷嘴。
消防软管应2 ½ “停工的单位类型。消防栓软管连接应女性
2 ½ “轮螺纹接头,以适应消防栓出水口。消防喉,应提供在三十米
长度为3 %的消防栓。软管应兴建中的高韧性聚酯纱
一高品位蒸汽vulcanised合成橡胶衬里,编造符合DIN 14811 & pren
1924-1 。
软管喷嘴应纳入喷射控制/切断阀。喷嘴应2 ½ “进
和制造由铝合金与提示,在聚酰胺材料。
消防喉联轴器及裁员单位的软管,应按照符合BS 336和BS恩
671-2 ,提供的:
安格斯消防有限公司
thame园道
thame
牛津郡
ox9 3rt
联合王国
http://www.angusfire.co.uk
电子邮件: general.enquiries @ kiddeuk.co.uk
电话: +44 ( 0 ) 1844214545
传真: +44 ( 0 ) 1844213511 / 2
或经核准的同等学历。
消防设备机柜
灭火设备应储存/位于指定的永久性防火
战斗设备机柜,除非另有指示。要求消防
战斗设备机柜设定为以下;
承包者应提供并安装永久柜储存的所有救火
设备(消防喉辘,喷嘴,阀门钥匙,胶管扳手等) 。 1
设备内阁完成与上述设备应安装毗邻每
地上消防栓。该设备机柜应大小750 x 750 x 300毫米和
兴建从1.5毫米热浸镀锌碳钢板;红色喷粉。字母a
打破玻璃应提供给使进入内阁中,除了一个关键锁定
进入设施。内阁应包括一个中央窗口(大小260 x二百六毫米) ,以查看
的内容,内部消防喉辘的支持PIN ,立场和相应的捏造。
每个内阁应包含
• 3软管长度
•胶管扳手
•阀门扳手
• 3软管喷嘴
• 1泡沫免费灭火器(概述在第5.4 )
• 1干的权力灭火器(概述在第5.4 )
• 1二氧化碳灭火器(概述在第5.4 )