电力英语翻译

1.Voltagesa.General.RefertoANSIStandardC84.1forvoltageratingsfor60Hzelectricpowersyst... 1. Voltages
a. General.
Refer to ANSI Standard C84. 1 for voltage ratings for 60 Hz electric power systems and equipment. In addition, the standard lists applicable motor and motor control nameplate voltage ranges up to nominal system voltages of 13.8 kV.
b. Generators.
Terminal voltage ratings for power plant generators depend on the size of the generators and their application. Generally, the larger the generator, the higher the voltage. Generators for a power plant serving an Army installation will be in the range from 4160 volts to 13.8 kV to suit the size of the unit and primary distribution system voltage. Generators in this size range will be offered by the manufacturer in accordance with its design, and it would be difficult and expensive to get a different voltage rating. Insofar as possible, the generator voltage should match the distribution voltage to avoid the installation of a transformer between the generator and the distribution system.
c. Power plant station service power systems.
(1) Voltages for station service power supply within steam electric generating stations are related to motor size and, to a lesser extent, distances of cable runs. Motor sizes for draft fans and boiler feed pumps usually control the selection of the highest station service power voltage level. Rules for selecting motor voltage are not rigid but are based on relative costs. For instance, if there is only one motor larger than 200 hp and it is, say, only 300 hp, it might be a good choice to select this one larger motor for 460 volts so that the entire auxiliary power system can be designed at the lower voltage.
(2) Station service power requirements for combustion turbine and internal combustion engine generating plants are such that 208 or 480 volts will be used.
d. Distribution system.
The primary distribution system for an Army installation with central in house generation should be selected in accordance with TM 5-811 -l/AFM 88-9.
展开
itarcy
2011-03-20 · TA获得超过266个赞
知道小有建树答主
回答量:382
采纳率:0%
帮助的人:487万
展开全部
1. Voltages
电压
a. General.
概述
Refer to ANSI Standard C84. 1 for voltage ratings for 60 Hz electric power systems and equipment. In addition, the standard lists applicable motor and motor control nameplate voltage ranges up to nominal system voltages of 13.8 kV.
60Hz电力系统和设备的额定电压,参见ANSI标准C84.1。另外,该标准列出了标称系统电压不超过13.8kv的适用发动机(电机)和发动机控制铭牌电压。
b. Generators.
发电机
Terminal voltage ratings for power plant generators depend on the size of the generators and their application. Generally, the larger the generator, the higher the voltage. Generators for a power plant serving an Army installation will be in the range from 4160 volts to 13.8 kV to suit the size of the unit and primary distribution system voltage. Generators in this size range will be offered by the manufacturer in accordance with its design, and it would be difficult and expensive to get a different voltage rating. Insofar as possible, the generator voltage should match the distribution voltage to avoid the installation of a transformer between the generator and the distribution system.
发电机及其应用。通常,发电机越大,则电压越高。供应军事装置的电厂发电机电压在4160伏到13.8千伏,适合机组和一级(主要)配电系统电压。该规格范围的发电机由制造商根据其设计予以提供。选用其它额定电压则比较困难而且价格昂贵。发电机电压应尽可能与配电电压匹配,省去在发电机和配电系统之间加装变压器的需要。
c. Power plant station service power systems.
电站供电系统
(1) Voltages for station service power supply within steam electric generating stations are related to motor size and, to a lesser extent, distances of cable runs. Motor sizes for draft fans and boiler feed pumps usually control the selection of the highest station service power voltage level. Rules for selecting motor voltage are not rigid but are based on relative costs. For instance, if there is only one motor larger than 200 hp and it is, say, only 300 hp, it might be a good choice to select this one larger motor for 460 volts so that the entire auxiliary power system can be designed at the lower voltage.
蒸汽发电电站内部供电电压与发动机规格有关,而与电缆布线距离的关系稍微远一点。抽风机和锅炉给水泵的电动机规格通常决定了电站的最高供电电压。发动机电压选择规则并不严格,而是根据相对成本。例如,如果只有一台200hp以上的发动机,比如只有300hp,那么最好将该更大的发动机用于460伏,从而整个辅助电力系统(厂用电系统)可以在更低的电压水平进行设计。
(2) Station service power requirements for combustion turbine and internal combustion engine generating plants are such that 208 or 480 volts will be used.
关于燃气轮机和内燃发动机发电厂的电站供电电压要求,将使用208或480伏。
d. Distribution system.
配电系统
The primary distribution system for an Army installation with central in house generation should be selected in accordance with TM 5-811 -l/AFM 88-9.
中心内部发电(这句不能肯定)的军事装置的一级(主要)配电系统按照TM 5-811-1/AFM 88-9选择。
诸葛狗蛋
2011-03-20 · TA获得超过1.4万个赞
知道大有可为答主
回答量:2116
采纳率:0%
帮助的人:641万
展开全部
1。电压
一。将军。
ANSI标准C84指电压额定值。1为60赫兹电力系统和设备。此外,标准列出适用电机和电机控制铭牌上标称系统电压范围内各种千伏电压。
b。发电机。
终端电压额定值电厂发电机依靠发电机的大小及其应用。一般来说,更大的发电机,电压越高。对某电厂的发电机组安装服务的军队将会是在范围从耶稣伏到13.8千伏来适应这种尺寸的单位和主配电系统电压。发电机在这个大小范围将提供由制造商按照其设计的,它将是困难和昂贵的,会得到一个不同的电压等级。只要可能,把发电机电压应与电网电压,避免了安装一个变压器,发电机之间的分配制度。
c。电厂站服务动力系统。
(1)电源电压为站内蒸汽服务相关电气电站的发电量,电机尺寸和较小的程度上,距离电缆脱钩。汽车大小,用以球迷和锅炉给水泵的选择通常控制站服务能力的最高电压水平。规则不严格选择电机电压但是基于相关的成本。比如,如果只有一个电机大于200点的生命,它是,姑且说,只有300点的生命,它可能是一个很好的选择这一更大的电机为460伏特从而使整个辅助动力系统设计可以在更低的电压。
(2)站服务能力要求涡轮和内燃机燃烧发电厂就是如此,208或480伏将会被使用。
d。配电系统。
在初次分配系统为一军事装置与中央在房子一代选择应依照5-811 -l / AFM 88-9 TM。
已赞过 已踩过<
你对这个回答的评价是?
评论 收起
吞噬的╮想菍
2011-03-27 · TA获得超过237个赞
知道答主
回答量:69
采纳率:0%
帮助的人:50.1万
展开全部
(1)电源电压为站内蒸汽服务相关电气电站的发电量,电机尺寸和较小的程度上,距离电缆脱钩。汽车大小,用以球迷和锅炉给水泵的选择通常控制站服务能力的最高电压水平。规则不严格选择电机电压但是基于相关的成本。比如,如果只有一个电机大于200点的生命,它是,姑且说,只有300点的生命,它可能是一个很好的选择这一更大的电机为460伏特从而使整个辅助动力系统设计可以在更低的电压。
(2)站服务能力要求涡轮和内燃机燃烧发电厂就是如此,208或480伏将会被使用。
d。配电系统。
在初次分配系统为一军事装置与中央在房子一代选择应依照5-811 -l / AFM 88-9 TM。
已赞过 已踩过<
你对这个回答的评价是?
评论 收起
周迈克picholin
2011-03-30
知道答主
回答量:12
采纳率:0%
帮助的人:0
展开全部
jkljl;jkl;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;
已赞过 已踩过<
你对这个回答的评价是?
评论 收起
收起 更多回答(2)
推荐律师服务: 若未解决您的问题,请您详细描述您的问题,通过百度律临进行免费专业咨询

为你推荐:

下载百度知道APP,抢鲜体验
使用百度知道APP,立即抢鲜体验。你的手机镜头里或许有别人想知道的答案。
扫描二维码下载
×

类别

我们会通过消息、邮箱等方式尽快将举报结果通知您。

说明

0/200

提交
取消

辅 助

模 式